Dear Electric Power and Transmission Forum:
As part of our HILS testing we are operating 4 Bosch HCS01 servo drives (24VDC for control, 230VAC single phase for motor supply)and their corresponding AC motors in an office-type environment.
The earth leakage in the office has a trip sensitivity of 30 mA.
The operation of all the drives results in frequent trips of the earth leakage which needs to be resolved so we can continue with our development.
I have not measured the magnitude of the leakage current since we do not have the required equipment.
From what I understand we should have a type B RCBO breaker with a higher trip sensitivity, presumably around 300mA, which will help minimize or eliminate the trips. However, presumably those levels of current could be dangerous to personnel? If so is there a way to handle the operational leakage current without increasing the trip sensitivity? I have heard of people using UPS's, where the 230VAC supply to the drives runs via a UPS but I'm not sure if this is a viable option?
Any suggestions would be greatly appreciated.
David
As part of our HILS testing we are operating 4 Bosch HCS01 servo drives (24VDC for control, 230VAC single phase for motor supply)and their corresponding AC motors in an office-type environment.
The earth leakage in the office has a trip sensitivity of 30 mA.
The operation of all the drives results in frequent trips of the earth leakage which needs to be resolved so we can continue with our development.
I have not measured the magnitude of the leakage current since we do not have the required equipment.
From what I understand we should have a type B RCBO breaker with a higher trip sensitivity, presumably around 300mA, which will help minimize or eliminate the trips. However, presumably those levels of current could be dangerous to personnel? If so is there a way to handle the operational leakage current without increasing the trip sensitivity? I have heard of people using UPS's, where the 230VAC supply to the drives runs via a UPS but I'm not sure if this is a viable option?
Any suggestions would be greatly appreciated.
David