JuanBC
Electrical
- Nov 28, 2017
- 141
Hello,
I would like your opinion regarding the following situation:
In a facility we are building (almost finished) someone designed a 13.2kV outdoor substation with (1) incoming overhead line entering through a recloser, and (7) outgoing feeders also equipped with reclosers.
All the reclosers are identical (ABB OVR-15 rated 600Amps with a RER-615 controller).
(4) of the reclosers are feeding "small" transformers (primary current = 8.7A @13.2kV)
Previous to the startup we discovered that the minimum setting for the recloser primary current is 24A, and therefore there is no way to protect this (4) transformers (protection functions are based on this sitting)
I will appreciate your ideas to find a nice solution. Find attached a simplified one-line diagram
Best regards,
JBC
.......
"The more I read, the more I acquire, the more certain I am that I know nothing"
I would like your opinion regarding the following situation:
In a facility we are building (almost finished) someone designed a 13.2kV outdoor substation with (1) incoming overhead line entering through a recloser, and (7) outgoing feeders also equipped with reclosers.
All the reclosers are identical (ABB OVR-15 rated 600Amps with a RER-615 controller).
(4) of the reclosers are feeding "small" transformers (primary current = 8.7A @13.2kV)
Previous to the startup we discovered that the minimum setting for the recloser primary current is 24A, and therefore there is no way to protect this (4) transformers (protection functions are based on this sitting)
I will appreciate your ideas to find a nice solution. Find attached a simplified one-line diagram
Best regards,
JBC
.......
"The more I read, the more I acquire, the more certain I am that I know nothing"