EJP-21
Mechanical
- Apr 27, 2020
- 25
Hello,
Im working on a project that has a kitchen that i considered to be ordinary hazard 1 however,
the architect, based on their schedules did not provide an automatic closing doors and the partition walls has 0A - N/A fire rating.
what options do i have other than requesting for them to provide a fire rated automatic closing doors.
is Adjacent Hazard 12.3 NFPA 13 (2013 Ed.) applicable in this situation where i need to extend 15ft from the perimeter?
or should use the minimum hydraulic area calculated?
See pic below.
Thank you
Room Design Method - 11.2.3.3 NFPA 13 (2013 Ed.)
Im working on a project that has a kitchen that i considered to be ordinary hazard 1 however,
the architect, based on their schedules did not provide an automatic closing doors and the partition walls has 0A - N/A fire rating.
what options do i have other than requesting for them to provide a fire rated automatic closing doors.
is Adjacent Hazard 12.3 NFPA 13 (2013 Ed.) applicable in this situation where i need to extend 15ft from the perimeter?
or should use the minimum hydraulic area calculated?
See pic below.
Thank you
Room Design Method - 11.2.3.3 NFPA 13 (2013 Ed.)