Single story building with sprinkler heads dated 1908 and a dry valve I've never encountered before.
The branch lines do not end in 3/4" pipe but 1/2" I kid you not. Never saw this before.
Here is what we have:
Used to be a ceiling with upright (conventional) sprinklers in the joist space but what the owner wants to do, in order to keep some sort of historical tax credit or what he told me, is keep half of the building open while half will have drywall ceilings. We have a wood beam and on the far side of the beam will be drywall attached to the bottom of the joists while the near side will remain open.
I don't see how we could install a 13R system with the open joists like they are given their depth. As you can see the depth is between two and three feet at the beam but the way the trusses are constructed we have big time obstructed construction.
And as much as I would like to use the existing system the upright sprinklers, both the uprights feeding the old concealed space and the heads below the ceiling, appear to be 7'-6" OC. There goes simply replacing the uprights with upright residentials where the minimum spacing is 8'-0". We would have to go 15' between heads plugging heads where needed.
As far as we can tell the last time the system was operational was 1985.
Bays are 25' wide with 3 lines per bay so head spacing is about 63 sq ft.
I am thinking the owner drywall below the joist and we install residential uprights which I think I can make work as the existing is staggered heads.
Oh, the building was only 40 years old when I was born so it really isn't that old.... am I historical?
The branch lines do not end in 3/4" pipe but 1/2" I kid you not. Never saw this before.
Here is what we have:
Used to be a ceiling with upright (conventional) sprinklers in the joist space but what the owner wants to do, in order to keep some sort of historical tax credit or what he told me, is keep half of the building open while half will have drywall ceilings. We have a wood beam and on the far side of the beam will be drywall attached to the bottom of the joists while the near side will remain open.
I don't see how we could install a 13R system with the open joists like they are given their depth. As you can see the depth is between two and three feet at the beam but the way the trusses are constructed we have big time obstructed construction.
And as much as I would like to use the existing system the upright sprinklers, both the uprights feeding the old concealed space and the heads below the ceiling, appear to be 7'-6" OC. There goes simply replacing the uprights with upright residentials where the minimum spacing is 8'-0". We would have to go 15' between heads plugging heads where needed.
As far as we can tell the last time the system was operational was 1985.
Bays are 25' wide with 3 lines per bay so head spacing is about 63 sq ft.
I am thinking the owner drywall below the joist and we install residential uprights which I think I can make work as the existing is staggered heads.
Oh, the building was only 40 years old when I was born so it really isn't that old.... am I historical?