esfo71
Mechanical
- Oct 23, 2010
- 8
Hello,
I have a question with concerns to Outdoor Air calculation. I have a Dictation Room within a hospital that is being reconfigured by the architects. This room has no exterior walls and is in the basement. The Volume of the room is about 3100 cubic feet and the Floor Area is about 400 square feet. I calculated the Heat Losses as follows:
Qlights = 3.41* (27*26W) *1*1*1 = 2400 BH
Qdesktop-lights = 3.41 * (5*50W)*1*1*1 = 900 BH
Qpeople = 5*250*1 = 1250 BH
Qequipment = 3.41 * (5*200W) *1*1*1 = 3500 BH
Qtotal = 8050 BH
CFM = 8050 / (1.085*(75-55)) = 371 CFM
The OA as per ASHRAE is recommended as 20CFM per person. Since there will be 5 people in the room, 100 CFM will be the amount the OA.
My question is the 100 CFM of OA added to the 371 CFM due to Heat Losses to make a total of 471 CFM of supply air or is 100 CFM part of the 371 CFM, that is, 371 CFM will be delivered to the space.
I would greatly appreciate it if someone could help me on this.
I have a question with concerns to Outdoor Air calculation. I have a Dictation Room within a hospital that is being reconfigured by the architects. This room has no exterior walls and is in the basement. The Volume of the room is about 3100 cubic feet and the Floor Area is about 400 square feet. I calculated the Heat Losses as follows:
Qlights = 3.41* (27*26W) *1*1*1 = 2400 BH
Qdesktop-lights = 3.41 * (5*50W)*1*1*1 = 900 BH
Qpeople = 5*250*1 = 1250 BH
Qequipment = 3.41 * (5*200W) *1*1*1 = 3500 BH
Qtotal = 8050 BH
CFM = 8050 / (1.085*(75-55)) = 371 CFM
The OA as per ASHRAE is recommended as 20CFM per person. Since there will be 5 people in the room, 100 CFM will be the amount the OA.
My question is the 100 CFM of OA added to the 371 CFM due to Heat Losses to make a total of 471 CFM of supply air or is 100 CFM part of the 371 CFM, that is, 371 CFM will be delivered to the space.
I would greatly appreciate it if someone could help me on this.