Using the "average" head is meaningless, because the decrease in WSE is not linear. You have to do the routing calcs (or integrate the discharge vs time) to determine the volume and WSE at any given time. Since the head is decreasing asymptotically, it will take an
infinite time to empty 100% of the pond volume, which is what your HydroCAD model is (correctly) telling you.
This points out a common problem with many WQV regulations: Since it can take a
very long time for a pond to empty completely, the WQV requirement should be written in terms of discharging a high percentage of the volume (say 95%). Attempting to measure the discharge time for 100% volume is problematic, as you have experienced.
To further illustrate the challenge, consider these seemingly insignificant variations:
1) Place the orifice slightly below the bottom of the pond. Even 0.01 feet below the storage will ensure a finite draw-down time, because the head never drops below 0.01 feet until the entire volume has discharged.
2) Sloping the bottom of the pond slightly (rather than using a flat bottom) has a similar effect, maintaining a larger head for very small volumes.
Of course, if your orifice is above the bottom of the pond you cannot employ either of these adjustments and you will need to accept the reality of an infinite time to empty 100% of the volume.
Peter Smart
HydroCAD Software