Due the lack of information... just a guess to see if I can help.
I reckon that the client would want to know if the system is capable of providing enough water fot three atack hoses.
So the aproach in that case would be to define what is the minimun requirement of pressure and flow for a hose. For example, the pressure would be from 65-100psi, and the flow from 95-250gpm for each hose. You could get that from brigade, fire service people or local regulations. (In my case, Costa Rica, fire service recommends that 1-1/2 hose for occupants use have at least 65psi and 95-100gpm, and the 2-1/2 hose requirements depends a lot on the specific case (in general 250gpm with 85-175 psi, see also NFPA 14).
But as others have said it depends a lot on the hoses, also on the hose nozzles, distances, etc. and who is going to use the hydrants.
So you have to make hydraulic calculations to see if the system is capable of providing three selected worst case hose locations, and after the system is installed, to check it with actual flow and residual pressure measurements.
It seems that your 277gpm pump, that could be consider to be capable of delivering up to 140-150% (387-415gpm) @ 142psi, would not feed three 2-1/2 hoses, but maybe three 100gpm 1 1/2 hoses, but as I mentioned it depends a lot on your local conditions and requirements.