Hi,
We have 450HP, 400RPM, 4160V, 16 pole SCIM. This motor is directly coupled with a make-up gas compressor. Its nameplate says FLA as 81.5A. However, this motor never run at this FLA rather it always run at 88A. Manufactur was recently contacted and he said that the measured FLA was 88.9A @ 0.586 pf. Manufacturer has no satisfactory answer on why the PF is too low at full load. Relay was also set (115%) as per 88A not 81.5A. Two years ago, this motor was also re-wound. Recent routine monitoring shows that FLA is 94A @ 100% load and 85A @ 50% load. Original design had Class B but after re-wound it has now Class H insulation.
Concerns were raised that why it is drawing more than rated FLA and secondly would be safe to run continuously at 94A? Currently we do not RTD connected to show any temperature data.
Other than this high current issue this motor used to have no performance related issues. Bearing and other mechnical checks shows there are no mechnical issue with this motor. Another interesting finding was NLA which was measured as 77A and the manufacturer says that it is because of high number of poles. There is a discussion on replacing this machine or keep running it. How you see it? are there any test or calculations you recommend to do?
Any comments?
Thanks in advance.
We have 450HP, 400RPM, 4160V, 16 pole SCIM. This motor is directly coupled with a make-up gas compressor. Its nameplate says FLA as 81.5A. However, this motor never run at this FLA rather it always run at 88A. Manufactur was recently contacted and he said that the measured FLA was 88.9A @ 0.586 pf. Manufacturer has no satisfactory answer on why the PF is too low at full load. Relay was also set (115%) as per 88A not 81.5A. Two years ago, this motor was also re-wound. Recent routine monitoring shows that FLA is 94A @ 100% load and 85A @ 50% load. Original design had Class B but after re-wound it has now Class H insulation.
Concerns were raised that why it is drawing more than rated FLA and secondly would be safe to run continuously at 94A? Currently we do not RTD connected to show any temperature data.
Other than this high current issue this motor used to have no performance related issues. Bearing and other mechnical checks shows there are no mechnical issue with this motor. Another interesting finding was NLA which was measured as 77A and the manufacturer says that it is because of high number of poles. There is a discussion on replacing this machine or keep running it. How you see it? are there any test or calculations you recommend to do?
Any comments?