BlackJackJacques
Marine/Ocean
- Apr 5, 2018
- 76
We have three 37.5 kVA 480/120 single-phase transformers wired Delta-Wye to derive 208/120 at the secondary. At 37.5 kVA, the single-phase Voltage and Current at the primary is 480V x 78.125A. Configured in Delta, the Primary Line current is 1.732 x 78.125A = 135.3A - indicating a new kVA rating of 112.5 kVA (480V x 1.732 x 135.3A) or three times the kVA rating for one transformer. Is this reasoning correct....that the system VA rating for Delta Wye transformers 3-phase are always three times the rating of single phase transformer?
Thanks