Hi All,
I'm just querying a recent design I received from an engineering house which is for a 0.75kW Ex Na 400V star connected motor.
The reason I am concerned is that the design does not have a dedicated overload relay. -All that is present is 3x4A fuses and a contactor (no protection against single phasing, and overload functionality with 4A fuses is set at the equivalent of 2.7KVA??).
I've challenged this and they have said its ok but this seems wrong for a Hazardous area rated motor when I am used to seeing hazardous area rated motors with a service factor of 1 and quite strict thermal overload controls (need to prevent surface temps exceeding limits as we are a T3 - 200degree max surface temp site).
Or is this actually permissable? If so can you explain as I'm a bit lost?
Thanks!
I'm just querying a recent design I received from an engineering house which is for a 0.75kW Ex Na 400V star connected motor.
The reason I am concerned is that the design does not have a dedicated overload relay. -All that is present is 3x4A fuses and a contactor (no protection against single phasing, and overload functionality with 4A fuses is set at the equivalent of 2.7KVA??).
I've challenged this and they have said its ok but this seems wrong for a Hazardous area rated motor when I am used to seeing hazardous area rated motors with a service factor of 1 and quite strict thermal overload controls (need to prevent surface temps exceeding limits as we are a T3 - 200degree max surface temp site).