controlnovice
Electrical
- Jul 28, 2004
- 976
Previous EE had a short circuit study completed by an outside firm. Resulting study found ~30 breakers that were over-dutied, their SCC rating was less than the available SCC at the bus.
Example: SCC available at 480V MCC bus is 33ka. Breaker feeding the MCC is rated at 25ka.
When I reviewed the study, they had incorrectly input some of the breakers. Some of the breakers are GE AKU-25 with fuses, which bumps up the breaker rating to 200ka.
But what about the molded case breakers feeding the individual loads from the MCC? If the SCC on the MCC is 33ka, the molded case breakers are 14ka (but the rating on the cubicle door indicates 25ka - someone here explain that?).
Do the molded case breakers need to be changed as well? If there is 33ka available on the bus, wouldn't it be available on the load side of the molded case breakers? Or, since the main breaker has a current limiting fuse, does that also protect the molded case breakers?
______________________________________________________________________________
This is normally the space where people post something insightful.
Example: SCC available at 480V MCC bus is 33ka. Breaker feeding the MCC is rated at 25ka.
When I reviewed the study, they had incorrectly input some of the breakers. Some of the breakers are GE AKU-25 with fuses, which bumps up the breaker rating to 200ka.
But what about the molded case breakers feeding the individual loads from the MCC? If the SCC on the MCC is 33ka, the molded case breakers are 14ka (but the rating on the cubicle door indicates 25ka - someone here explain that?).
Do the molded case breakers need to be changed as well? If there is 33ka available on the bus, wouldn't it be available on the load side of the molded case breakers? Or, since the main breaker has a current limiting fuse, does that also protect the molded case breakers?