Overexcatation Trip at first energizing Transformer...7UT613

Status
Not open for further replies.

rayas91

Electrical
May 6, 2015
71
Friends ,

We re energizing MV Side with 15 KV /6,9 KV Auxiliary Transformer from 132 kV/15 KV Switchyard .But during the energizing, UAT Relay is trippinng from Overexcatation Protction.

I do not know why.Engineering side is sure about settings.
Transformer Nominal working Tap "14", It s trip at tap 14,but at the "9" tap no trip.

Can you help me please,

Relay is "7UT613"

 
Replies continue below

Recommended for you

Check the event reports on the relay. What is the voltage & frequency on tap 14?
 
At a first glance I would blame the settings. Would it be possible for you to show us the following settings: 4302 to 4313 (I assume it is version 4.xx relay)? Could you provide OLTC data (… kV +- … x …%)?

COMTRADE would be very useful as well (to see the voltage signal, which stage has tripped U/f> or U/f>>, tripping time etc.).
 
Krustabas, Thank you for interested to reply my problem.


I fixed problem today..Actually it s my fault.

You know there s primary and secondary side of transformer.15/6,9 kv ....Normally the relay gets voltage information on 15 kv side...But i choosed 6,9 side ...so V/Hz seems %214-217....V/F seems 2,14-2,17...I changed it and everythgn ok now...


Thank you again ..and sorry for my english...
 
Thanks for reporting back to us.

Bill
--------------------