Friends ,
We re energizing MV Side with 15 KV /6,9 KV Auxiliary Transformer from 132 kV/15 KV Switchyard .But during the energizing, UAT Relay is trippinng from Overexcatation Protction.
I do not know why.Engineering side is sure about settings.
Transformer Nominal working Tap "14", It s trip at tap 14,but at the "9" tap no trip.
Can you help me please,
Relay is "7UT613"