We shall install an overhead line running about ~7km west as well as ~5 km to the North East. The O/H line shall be 13.8kV, high resistance, 3 wire, 60Hz, and we shall use Partridge 266.8 MCM ACSR.
We shall also use an overhead ground conductor wire and I am wondering if we should go with bare copper or ACSR for the ground conductor. I've read that:
My question is why would Copper be used? ACSR is much more economical. Is there an advantage of Copper over ACSR for the grounding conductor? Can someone please elaborate?
Thanks,
Majesus
We shall also use an overhead ground conductor wire and I am wondering if we should go with bare copper or ACSR for the ground conductor. I've read that:
From McGraw-Hill's National Electrical Safety Code (NESC) handbookMany utilities use copper for the entire length of the grounding conductor. Some utilities use aluminum or ACSR. Typically, the aluminum or ACSR is used above grade, spliced to copper, which then runs below grade. Some utilities utilize copper-coated steel. Copper substitutes have become popular due to copper theft.
My question is why would Copper be used? ACSR is much more economical. Is there an advantage of Copper over ACSR for the grounding conductor? Can someone please elaborate?