EETD
Electrical
- Jul 9, 2004
- 10
Hi all,
I have a client who wishes to consider the cost change associated with changing from underground distribution to overhead for the following system:
1)Utility Transmission Voltage, 69kV
2)Plant Distribution Voltage, 4.16kV
3)Main Plant Switchgear:
- Main/Tie/Main (N.O. Tie)
- 4000A Main/Tie Bkrs
- 2-1200A Bkrs & 2-2000A Bkrs on one side of Tie
- 3-2000A Bkrs on other side of Tie
- System is low resistance grounded at main substation transformer secondary.
4) All but 1-1200A Feeder need to be distributed into the plant, the main switchgear is not centrally located.
5) Conductor sizes for underground installation of each feeder have been determined as follows:
1200A Bkr - 5 Sets 750kCMIL with #4/0 Gnd
2000A Bkr - 7 Sets 750kCMIL with 250kCMIL Gnd
Questions:
1) Obviously the conductor sizes and number of sets per phase can be decreased for an aerial installation. However, with the requirement to distribute six 5kV feeders into the plant...would a pole/tower structure installation even be practical? Possible?
2)Is this voltage practical for overhead distribution at these loads?
3)Does anyone know of where I might possibly find published cost comparison information (% difference, Overhead vs. Underground) for a system similar to this?
Your thoughts and opinions are appeciated.
Many thanks,
EETD
I have a client who wishes to consider the cost change associated with changing from underground distribution to overhead for the following system:
1)Utility Transmission Voltage, 69kV
2)Plant Distribution Voltage, 4.16kV
3)Main Plant Switchgear:
- Main/Tie/Main (N.O. Tie)
- 4000A Main/Tie Bkrs
- 2-1200A Bkrs & 2-2000A Bkrs on one side of Tie
- 3-2000A Bkrs on other side of Tie
- System is low resistance grounded at main substation transformer secondary.
4) All but 1-1200A Feeder need to be distributed into the plant, the main switchgear is not centrally located.
5) Conductor sizes for underground installation of each feeder have been determined as follows:
1200A Bkr - 5 Sets 750kCMIL with #4/0 Gnd
2000A Bkr - 7 Sets 750kCMIL with 250kCMIL Gnd
Questions:
1) Obviously the conductor sizes and number of sets per phase can be decreased for an aerial installation. However, with the requirement to distribute six 5kV feeders into the plant...would a pole/tower structure installation even be practical? Possible?
2)Is this voltage practical for overhead distribution at these loads?
3)Does anyone know of where I might possibly find published cost comparison information (% difference, Overhead vs. Underground) for a system similar to this?
Your thoughts and opinions are appeciated.
Many thanks,
EETD