Dear All,

In the prepared shop drawings for steel reinforcement by supplier he did the following:
for columns, overlap in the middle of column
while in shear walls overlap at the bottom of verticals


The Slab is PT,

I do understand the for both columns and shear walls the zero moment will be at center, so why both have different overlap location.

The Tower is 60 Floors height

regards
 
Replies continue below

Recommended for you

From a constructability perspective, I believe that the most convenient location for vertical bar laps in both columns and walls is at the top of slab elevation. It makes for an easy resting place for the upper cage. So, baring other considerations, that's what I'd expect for both columns and walls.

In some seismic regimes, splices in columns resisting lateral displacement are located at or near column mid-height in order to avoid the high moment regions as you've suggested. Might that be the case for your project?

Lastly, note that the vertical rebar in most tall shear walls is governed by cantilever flexure of those walls over the entire building height. As such, there really is no zero moment condition at each floor in general.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 