dhenderson2014
Chemical
We have recently completed a LOPA study of a gas (predominantly methane) system and have found that one of the knockout drums is not adequately protected from over-pressure, based on our tolerability criteria. We have concluded that the drum requires an order of magnitude risk reduction for the scenario in which the split-range control loop fails to danger i.e. the inlet PCV fails in the wide-open position.
I have attached a sketch of the system in question for your understanding.
Upstream pressure = 37barg
KO Drum design pressure = 7barg
KO Drum normal operating pressure = 4barg
Some conclusions thus far:
1) The split-range control loop is not a valid barrier as it is assumed to have failed to danger.
2) The high pressure alarm is not a valid barrier as there is insufficient process safety time. I have tried to take credit for this by installing an RO in the supply line to the KO drum. However, this is not feasible as, under normal operation, this would limit the flowrate to below the fuel gas demand of the downstream furnace.
3) Upstream pressure cannot be limited to below the design pressure of the KO drum as the DP across the inlet PCV under normal operation would not provide the required flow for the furnace.
At present, the only recommendation that we can think of is to install a SIL 1 independent high pressure trip on the inlet to the KO. I was wondering if anyone had any other 'clever' ideas for risk reduction before we implement the high pressure trip.
Thanks!
Thanks!