Hai
I wish to compensate for the kg/hr flow indication sent by a dp (orifice) meter.
I want to use the below formula
F_comp = F_act * (((T_ref * P_act)/(T_act*P_ref))^0.5)
F_ comp = compensated flow in kg/hr
F_act = actual flow in kg/hr form transmitter
T_ref = T_ref in degC + 273.15
P_ref = P_ref in kgf/cm2g + 1.033
T_act & P_act are operating pressure
What is the correct reference temp and pressure to use?
2 sets of information I have are
the design data in meter datasheet
calibration sheet of the transmitter where a 0 to 2500mmH2O at 20degC water was used calibrating from 0 to 100% of transmitter range.
Instrument engineers do have the correction but the underlying principle is not clear. I wanted to know the principle and correct quantities that must be used.