Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

panelized non load bearing studs in plane continuity 1

Status
Not open for further replies.

structSU10

Structural
Mar 3, 2011
1,062
Curious of others thoughts on this. Exterior cold form, panelized, come with exterior sheathing attached. The panels are not attached to each other in general, and at some locations they have a 14" gap between panels that will be closed with field installed sheathing.

To me I think track continuity would be good to have so panels will share load, but I can see the argument that it is not strictly required. What are others thoughts on this general arrangement?
 
Replies continue below

Recommended for you

If they're shear walls or the top track is acting as a collector for shear walls along the same wall line, then you need continuity. Whether that's accomplished through a track splice (track is the collector) or fastening the panels to a continuous steel angle or some other "external" collector, it doesn't really matter.

If they aren't shear walls, then I wouldn't worry too much about it.
 
Seconding phamENG's comment. If they're shear walls, splice your top track for continuity or attach to something that can act as a collector. If they are non-structural, not much to worry about. I like to specifically state that the ends of the tracks need to be anchored to structure so you aren't cantilevering the track.

Judgement-In-Training
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor