PanelView Plus 1000 Alarm list not working ???

Status
Not open for further replies.

RayfromIntech

Electrical
Jun 2, 2003
34
Last remainning issue on this project. Now i know my tags are comming in the touch screen.

What have I forgotten to do^

What I have done so far.

Configured the alarm setup (triggers and so on)
Pointed that to the alarm list page
Tags are all bits so I put bit for trigger type.
In the message i put trigger value to 1
Triggers and messages are all there.

Did a page with alarm list.
Why is no alarm being generated.???

Thanks ray


 
Replies continue below

Recommended for you

Try changing the trigger type from 'bit' to 'value'.

The following is from the Rockwell Knowledge base,
E26036864:
Problem: Alarm trigger causes error when project is run.
Cause: Alarm trigger is set to bit triggered in Alarm setup, and trigger tag is digital. RSView ME is expecting Block tags when it sees bit triggered selected.
Verify:
Cure: If you are using digital tags, select Value as the trigger type in Alarm setup. This scenario is common when using OPC to communicate with a device, since OPC does not support Block tags.

 