robthecob
Electrical
- May 12, 2005
- 7
We are measuring 200 amps in the ground conductors from the 480 volt substation ground bus to the MCC ground buses. The 480 volt sub is a double-ended substation with two 3000 kVA 12.5kV-480 volt transformers. Each half of the substation powers three 1600 bus MCCs, each with 1000 amps of load. The MCC feeder cables are four 1/C-500MCM cables/phase routed in cable trays for 300'. The MCC feeder cables have been installed in the cable trays with the A phase cables grouped together (in one plane), then the B phase cables grouped together, then C phase cables grouped together with the single 1/C-4/0 ground conductor laying on top. I realize this is not the proper method for installing three phase cables in tray, but I inherited this problem. The motors powered from the six MCCs are connected to the MCC starters via 3/C with ground tray cable with approximately 15 amps measured in each ground conductor to the motor. The ground current to the motors is almost identical for each motor on the various MCCs.
The transformer neutrals are connected to the substation ground bus via busbar. The substation is located 150' behind the plant with elevated cable trays routing the 480 volt TC cables to the MCCs inside the plant. The six MCCs are located close together inside the plant electrical room with cable tray distribution from the MCCs to the motors. The cable trays are bonded to the MCC ground buses and each other.
I suspect the MCC parallel feeder cable routing is the problem, but I find it hard to believe it would be to this magnitude. Any ideas?
The transformer neutrals are connected to the substation ground bus via busbar. The substation is located 150' behind the plant with elevated cable trays routing the 480 volt TC cables to the MCCs inside the plant. The six MCCs are located close together inside the plant electrical room with cable tray distribution from the MCCs to the motors. The cable trays are bonded to the MCC ground buses and each other.
I suspect the MCC parallel feeder cable routing is the problem, but I find it hard to believe it would be to this magnitude. Any ideas?