podobing
Electrical
- Jan 28, 2013
- 49
Good Morning,
I have a question regarding the partial replacement of parallel conductors feeding a three phase, 200 HP, 575 volt motor.
The original installation used parallel 500 kcm aluminum cables that were 1800 feet long. The cables were damaged and were going to be replaced with parallel 350 kcm copper cables. If will be very difficult to change the aluminum cables in their entirety, so it was decided to install an adequately sized junction box at the 1000 foot mark. There are two options being considered:
Option 1 - Install a power block with 4 ports per phase in the junction box. Each port would be properly sized and rated for either copper or aluminum conductors. This would result in the two 1000' long copper conductors being in parallel, and then that combination would be in series with the parallel combination of the two 800' long aluminum conductors per phase.
Option 2 - Install a mechanical crimp reducing splice sleeve in each conductor. Each side of the splice sleeve would be properly sized and rated for each conductor type and size. This would result in two 1800' long conductors (1000'copper and 800' aluminum) being placed in parallel per phase.
My question is: Which option (or do both options) comply with NEC 310.15(H)(2)or other NEC requirement that I have not considered?
310.15(H)(2)states: "The paralleled conductors in each phase, polarity, neutral, grounded circuit conductor, equipment grounding conductor, or equipment bonding jumper shall comply with all of the following:
1) Be the same length;
2) Consist of the same conductor material;
3) Be the same size in circular mil area;
4) Have the same insulation type; and
5) Be terminated in the same manner."
What do you think?
Thank you,
Podo
I have a question regarding the partial replacement of parallel conductors feeding a three phase, 200 HP, 575 volt motor.
The original installation used parallel 500 kcm aluminum cables that were 1800 feet long. The cables were damaged and were going to be replaced with parallel 350 kcm copper cables. If will be very difficult to change the aluminum cables in their entirety, so it was decided to install an adequately sized junction box at the 1000 foot mark. There are two options being considered:
Option 1 - Install a power block with 4 ports per phase in the junction box. Each port would be properly sized and rated for either copper or aluminum conductors. This would result in the two 1000' long copper conductors being in parallel, and then that combination would be in series with the parallel combination of the two 800' long aluminum conductors per phase.
Option 2 - Install a mechanical crimp reducing splice sleeve in each conductor. Each side of the splice sleeve would be properly sized and rated for each conductor type and size. This would result in two 1800' long conductors (1000'copper and 800' aluminum) being placed in parallel per phase.
My question is: Which option (or do both options) comply with NEC 310.15(H)(2)or other NEC requirement that I have not considered?
310.15(H)(2)states: "The paralleled conductors in each phase, polarity, neutral, grounded circuit conductor, equipment grounding conductor, or equipment bonding jumper shall comply with all of the following:
1) Be the same length;
2) Consist of the same conductor material;
3) Be the same size in circular mil area;
4) Have the same insulation type; and
5) Be terminated in the same manner."
What do you think?
Thank you,
Podo