We plan to install two Deaerators in a steam plant each sized for 60% of full load. Plant normal load is 25 - 50% of full load. What is the best way to control steam and water into the Deaerators?
Currently, we plan to
1) pump water from condensate return through one valve controlled by Condensate Tank Level (with overide if Deaerator Storage Tank level is high). The flow will be split in the piping to both deaerators.
2) supply makeup water from softeners through one valve controlled by Deaerator Storage Tank Level. The flow will be split in the piping to both deaerators.
3) supply steam through one valve controlled by Deaerator Pressure. The flow will be split in the piping to both deaerators with orifice plates in each leg to help balance flow.
4) header the deaerator storage tanks together at the bottom to balance the level and pressure.
5) provide separate level transmitters on each Deaerator Storage Tank with averaging to the level control.
6) provide separate pressure transmitters on each Deaerator with averaging to the pressure control.
7) provide separate safety devices.
Normal operation will be both Deaerators online and operating at 5 PSI.
Question: Would it be better to use two Condensate valves, two Makeup Water valves and two Steam valves?
Thanks
Currently, we plan to
1) pump water from condensate return through one valve controlled by Condensate Tank Level (with overide if Deaerator Storage Tank level is high). The flow will be split in the piping to both deaerators.
2) supply makeup water from softeners through one valve controlled by Deaerator Storage Tank Level. The flow will be split in the piping to both deaerators.
3) supply steam through one valve controlled by Deaerator Pressure. The flow will be split in the piping to both deaerators with orifice plates in each leg to help balance flow.
4) header the deaerator storage tanks together at the bottom to balance the level and pressure.
5) provide separate level transmitters on each Deaerator Storage Tank with averaging to the level control.
6) provide separate pressure transmitters on each Deaerator with averaging to the pressure control.
7) provide separate safety devices.
Normal operation will be both Deaerators online and operating at 5 PSI.
Question: Would it be better to use two Condensate valves, two Makeup Water valves and two Steam valves?
Thanks