I have read the thread "Multiple Resistor Grounding" and have gleaned good facts. Big difference here is solid grounding. Perhaps after discussion, solid grounding will be ultimately the thing to go...
The power generation is islanded, consisting of three identical 2/3 pitch generators each rated at 200 kW, 600 V. We have a 3 phase, 3 wire system (no 347 V loads). There will be times when two of the generators will co-generate, sharing the load equally between them. Additionally, VArs will be equally shared using a reactive differential compensation scheme.
The grounding of the generators' star points will be solid; i.e. no intentional impedance. In the past, a current transformer in the star point of each generator has led to erroneous indications of "ground current", due to the voltage on the two online generators being different by a small amount, causing a circulating current to flow. Short of installing impedances to minimize this current flow, does anyone have any suggestions to minimize/stop this flow or to relay appropriately so as to not get false indications? Suggestions have been varied, like tying neutrals together and then going to earth through ground fault ct (one ct source feeding three relays), and also using 3rd harmonics present in circulating current to discriminate from “true” ground faults.
Client has used solid grounding and is reluctant to change unless compelling reasons are provided. Generator manufacturer is providing bracing suitable for solid grounding.
Any ideas/suggestions?
The power generation is islanded, consisting of three identical 2/3 pitch generators each rated at 200 kW, 600 V. We have a 3 phase, 3 wire system (no 347 V loads). There will be times when two of the generators will co-generate, sharing the load equally between them. Additionally, VArs will be equally shared using a reactive differential compensation scheme.
The grounding of the generators' star points will be solid; i.e. no intentional impedance. In the past, a current transformer in the star point of each generator has led to erroneous indications of "ground current", due to the voltage on the two online generators being different by a small amount, causing a circulating current to flow. Short of installing impedances to minimize this current flow, does anyone have any suggestions to minimize/stop this flow or to relay appropriately so as to not get false indications? Suggestions have been varied, like tying neutrals together and then going to earth through ground fault ct (one ct source feeding three relays), and also using 3rd harmonics present in circulating current to discriminate from “true” ground faults.
Client has used solid grounding and is reluctant to change unless compelling reasons are provided. Generator manufacturer is providing bracing suitable for solid grounding.
Any ideas/suggestions?