geliberman
Mechanical
- Jul 2, 2011
- 31
I've recently integrated a new pump at a boiler feed water plant that is in addition to three existing pumps.
Three old pumps are identical(2 motor driven and one steam turbine driven pumps) with 73m shut off head.
The new pump (Steam turbine driven) is smaller and have 58m shut off head.
When we use 2 steam driven pumps,(new and old) there is no problem, but when the third pump starts it will cause the new pump to work without flow and the pump check valve will fluctuate,and after a while the casing temperature will increase. the cavitation also occurs in the new pump.
I know that we have made a mistake in pump selection, but how can we solve the problem.
How we can change the system curve to use 2 old pump together with new pump?
is that possible to use ARC valve or it is better to use a control valve?
Three old pumps are identical(2 motor driven and one steam turbine driven pumps) with 73m shut off head.
The new pump (Steam turbine driven) is smaller and have 58m shut off head.
When we use 2 steam driven pumps,(new and old) there is no problem, but when the third pump starts it will cause the new pump to work without flow and the pump check valve will fluctuate,and after a while the casing temperature will increase. the cavitation also occurs in the new pump.
I know that we have made a mistake in pump selection, but how can we solve the problem.
How we can change the system curve to use 2 old pump together with new pump?
is that possible to use ARC valve or it is better to use a control valve?