Mbrooke
Electrical
- Nov 12, 2012
- 2,546
When transformers are paralleled, what effect if any do circulating currents have on deferential protection and other protective relaying?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Table1 of IEC 76-5
Rated KVA %
Up to 630 4.0
631-1250 5.0
1251-3150 6.25
3151-6300 7.15
6301-12500 8.35
12501-25000 10.0
25001-200000 12.5
B) Oil Filled
Table 10, C57.12.10
Without LTC With LTC
HV LV LV 2400 LV 2400and
BIL 420V and above above
60-110 5.75 5.5 ---
150 6.75 6.5 7.0
200 7.25 7.0 7.5
250 7.75 7.5 8.0
350 ----- 8.0 8.5
450 ----- 8.5 9.0
550 ----- 9.0 9.5
650 ----- 9.5 10.0
750 ----- 10.0 10.5