1
- #1
chris8591
Electrical
- Dec 16, 2002
- 3
What is the recommended practice for paralleling / transfering and splitting loads between two 132kV/11kV Transformers? The transformers are rated at 45MVA and carry loads of 15MW and 8MW in a split configuration. The transformers have a 14 tap OLTC and are normally coupled on the 132kV side, when paralleled they are coupled via 11kV circuit breakers and busbars.