Back when I was working with CAT, it was more of a Latin American District policy, mainly based on the fact that we had a very hard time finding shops to do competent rewinds and repairs to larger generators, from a cost and time standpoint, plus trying to prevent repeat failures, replacement with new was often used. EAME, the Europe, Middle East and Africa District also applied a similar policy in many areas of the world.
CAT Power Generation had a hard time in dealing with this particular issue, we put a lot of modular and permanent plants in that in my opinion we not properly grounded or protected, but went into service anyway, and we had a fair number of failures. In older projects with more physically robust generators we had fewer problems, in newer plants with "value engineered" generators we experienced more problems and tail end failures. We ate lots of diodes, killed lots of AVR's and I pulled a lot of tail ends, not sure exactly where the cost saving was.
Did learn that a well thought out protection scheme, properly tuned and commissioned control systems, and good engineering practises helped prevent failures, too bad too many times the cost of doing it right the first time prevented things from working the way it should. Of course many of our competitors had similar issues as the drive to reduce cost caught a lot of us.
I did a lot of modular and portable multiple units systems all over the world, mostly 480V and 12.47kV for CAT, we usually opted not to use grounding resistors or reactors on systems with less than four units, at four units and above the amount of available fault current was more than enough to kill a stator. Of course we did have two and three unit systems that had stator failures, so this wasn't a perfect solution.
To Mike6061, I know one of the criteria for the military mobile systems is to minimze cube and weight for transport, and generally the deployment of these systems was supposed to be "short duration", but as I'm sure you've seen, many of the plants go into service for longer periods of time, and are exposed to more potential risk for faults, and don't get the PM maintenance they should while in service in those conditions. The application of proper grounding protection would limit potential of catastrophic failure in the event of a ground fault, so far you've been lucky, but it will eventaully catch up, and Col Murphy has a lousy sense of humor and timing.
Lot of smart people above have given you some pretty helpful information, hope that helps.