Anyone familiar with Neplan? I got a 3 windings transformer rated at
1. 7.6/6.8/0.8MVA,
2. 18/11/0.415kV,
3. Uk(H/X)=12% to 6.8MVA base
4. Uk(H/Y)=5% to 0.8MVA base
5. Uk(X/Y)=7.5% to 0.8MVA base

May i know how to translate this to

Rated power in MVA.
12: primary-secondary,=6.8?
23: secondary-tertiary,=?
31: tertiary-primary.=0.8?

Rated positive sequence short-circuit voltage with
respect to Sr12, Sr23, Sr31 and Ur1, Ur2, Ur3.
12:primary-secondary,= ?
23: secondary-tertiary,=?
31: tertiary-primary.=?
 
Replies continue below

Recommended for you

The rated power is the winding power, so the minor rated power in the power flow is the one you are looking for (0.8MVA).

Z12=12%
z23=7.5%
Z13=5%
 
Just be careful on the base. You indicated none of MVA values are on the primary base.
So, check the transformer test report to make sure.
 
I don't think so. When going from a lower MVA base to a higher MVA base the per unit impedance of the same ohmic value goes up. Someplace something that should have be multiplied was divided.
 
tiewrc said:
Anyone familiar with Neplan?
No.
tiewrc said:
Rated positive sequence short-circuit voltage with
respect to Sr12, Sr23, Sr31 and Ur1, Ur2, Ur3.
12:primary-secondary,= ?
23: secondary-tertiary,=?
31: tertiary-primary.=?
Voltage where? On the unfaulted winding?

You'll have to convert the winding-to-winding impedance figures to an equivalent star circuit. With a little simultaneous linear equation chicken scratch on the back of an envelope, I get:

Zh-o = 0.0475 pu
Zx-o = 0.0725 pu
Zy-o = 0.0025 pu

Now, for a source of 1.0V pu on H and a balanced fault on X,
the voltage on the unfaulted winding, Vy is:

Vy = Vh ( Zh-o / ( Zh-o + Zx-o ) ) = 0.604 pu

Hint: If you draw the one-line diagram for the fault, it looks like a simple voltage divider.

If this is NOT what you were after, then ignore everything I've said.
 
let me know if I'm wrong:

Z=Zpu1*Zb1=Zpu2*Zb2 Z=U^2/S

Zpu2=Zpu1*(Ub1^2/Sb1)/(Ub2^2/Sb2)

If the impedance in pu it's higher or lower depends of U^2/S ratio

Anyway, I think those values are odd, so maybe the Uk given are not in the base you are saying

 
Typically 3 winding xmfs (US standards...don't know your brand) the M/Kva ratings are of the winding. You can look at it like it has 2 secondaries. One you "put in" 7.6M, one you "can get" 6.8M from and one you "can get" .8M from.

We used to use these in remote substations: the third winding was for station power.

As far as the Z calcs go, these other guys are right on.

Steve
 
Tha calcs are Ok, but not the values.

3. Uk(H/X)=12% to 6.8MVA base
4. Uk(H/Y)=5% to 0.8MVA base
5. Uk(X/Y)=7.5% to 0.8MVA base

I thought the "to" was the base of the impedance after the pwrtran post.

I think that my first post is the right one
 