Parapet deflection

Status
Not open for further replies.

xez

Structural
Jan 4, 2012
43
What does everyone use as the minimum deflection limit for parapets? Footnote i in Table 1604.3 of the IBC allows cantilever members to have twice the deflection of the wall. In an application where the wall deflection limit is L/180, that would allow a parapet deflection of L/90. Does that seem a bit excessive assuming it isn't affected by other factors such as siding, stucco, etc.
 
Replies continue below

Recommended for you

If the siding is not affected by the deflection in terms of aesthetic damage or moisture I don't see why it would be excessive.
 
Parapets are usually not very high, so I don't recall ever checking the deflection of a parapet. But allowing a parapet to deflect twice as much as a simple span seems to make sense.

For a simple span:
M = wL[sup]2[/sup]/8; Δ = 5wL[sup]4[/sup]/384EI
So Δspan = 5ML[sup]2[/sup]/48EI

For a cantilever:
M = wL[sup]2[/sup]/2; Δ = wL[sup]4[/sup]/8EI
So Δcant = ML[sup]2[/sup]/4EI

The main reason to limit deflection is to limit curvature which would cause cracking in brittle finishes. Curvature = M/EI, so to maintain the same curvature in a cantilever or a simple span:
Δcant/Δspan = 12/5 = 2.4, a little more than 2.0​

Another reason to limit deflection is to limit P*δ, a moment magnifier. In the case of a parapet, P is very small and δ is about Δ/3 so that does not seem to be a concern.

This would suggest that if a simple span is permitted L/180 deflection, a cantilever should be permitted L/90.

BA
 
Great. Thank you for the feedback and explanation! This makes perfect sense.
 