Haynewp-
For an office use, even though the code seems to say that the partition load is included within the live load when using > 80 psf LL, I treat it as a dead load and non-reducible. This is probably conservative but on balance I will have little control over what partitions are put in over the useful life of the building.
Believe that the statistical unlikelihood of actually ever getting a full live load on the floor is what drives the code to allow partitions to be included when designing with a higher live load. This is a nice idea in theory, but I think it is confusing in everyday practice. (The old BOCA had the this same issue as the current IBC does now).
For example, if partitions are moveable this means that corridor locations can change. Code minimum office live loads for corridors (100 psf first floor, 80 psf upper floors) are higher than for just office space (50 psf). I therefore usually end up designing the entire floor area that is going to carry moveable partitions for the corridor load. Doing anything else will restrict how that portion of the building can be used, imho.
So for example, for a non-composite steel framed first floor office, for gravity design I will use 80 psf as the reducible live load, but also add 20 psf to whatever the other dead loads are. I consider this as using the equivalent of a 100 psf IBC office live load. If you have composite beams then the 20 psf is a superimposed dead load after the concrete is in.
I still design using ASD most of the time, so haven't done this with LRFD load factors. But if I was, would probably use the lower DL factor for the 20 psf partition load.
The other question this raises is how do you treat the 20 psf moveable partition load when calculating mass for seismic loads? Have to admit I usually don't include it, which perhaps is inconsistent. Most of the buildings I work on are three stories max in low seismic risk areas, so there probably would not be a significant difference in the lateral shear if it was included. But for a much taller structure in a higher seismic zone the difference in lateral load could be huge. Any one out there who does tall buildings out west care to comment further?
The best practice might be to always include the 20 psf partition load as part of the seismic mass, but I know of nothing in the literature that justifies keeping it in or out.
Good question.