jordon
Electrical
- Oct 4, 2006
- 3
Application: SCR-controlled Battery Charger.
Input power: 440 VAC, 60 Hz, 3 ph, 3-wire, 10 KW.
Output power: 42.3 VDC, 200 Amps.
Input Transformer: 440V pri. Δ, 44V sec. Y, 18-pulse (9-phase).
Links shows sketch of application and transformer winding configuration.
Link
I thought the 18-pulse transformer would eliminate most of the unwanted input current harmonics...
However, I'm still seeing harmonics, 5th, 11th, 17th, and 19th are all above 3% (5th and 17th being the highest, at 6%).
I would like suggestions on how to attenuate these harmonics to below 3% using a passive (RLC) AC filter on the 440V primary side.
Design papers, calculations, or rules of thumb are welcome.
Looking for a solution that is robust (allowable ~5-10% tolerance on selected RLC components).
Thanks.