Pellet boiler and PED
nale88
5
Greetings,
I'm an intern in my firm that makes pellet boilers, and they've put me in charge of CE issue. Needless to say, I'm in way over my head.
Anyways, could someone guide me a bit with PE directive, mainly with Article 1, section 3.6 (here are excludes from the Directive listed):
PED said:
equipment classified as no higher than category I under Article 9 of this Directive and covered by one of the following Directives. ...
and the Article 9 says:
PED said:
For the purposes of such classification fluids shall be divided into two groups in accordance with 2.1 and 2.2.
[li]2.1 Group 1 comprises of dangerous fluids. A dangerous fluid is a substance or preparation covered by definitions in Article 2 (2) of Council Directive 67/548/EEC of 27 June 1967 on the approximation of the laws, regulations and administrative provisions relating to the classification, packaging and labelling of dangerous substances. ... [/li]
[li]2.2. Group 2 comprises all other fluids not referred to in 2.1.[/li]
The thing is, I just simply cannot grasp the 3.6. Does that means that:
[li]if IT IS a dangerous fluid (it's category I), then it can be excluded from PED (b/c it falls under eg. Machinery);[/li] or
[li]if IT'S NOT a dangerous fluid (it's category II), and it falls under Machinery, than it can be excluded from PED[/li]
I have older reports for these pellet boilers from independent laboratories, and nobody even mentions PED.
Thank you.
The higher the category number, the greater the risk if something goes wrong. A dangerous fluid in a vessel moves up a category or two. If it's a safety related item, relief valve for instance, it will be Cat. IV and can possibly downgrade from there. I would suggest that you go online and search for the PED Guidelines, it is a free download and helps to clarify a lot of the clauses. I've found that many experts are confused by the PED and I'm far from one myself. One other thing I've run into is getting the people around me to understand the rules and the implications of the PED, esp. when it comes to the higher categories.
You are not reading carefully i think. If it's a dangerous fluid then it's GROUP I not CATEGORY I.
It is obvious that more restrictive for dangerous fluids!
Yes, you are right, after flipping through guide (like jwhit suggested), I've come to that conclusion. I just don't understand why would they link it to that section, instead of appropriate, containing the a.m. categories.
Well I think article 9 is quite clearly written. It says "..shall be classified by category in accordance with Annex II, according to ascending level of hazard.". Then goes on to explain that for the purpose of classification you need to know the fluid group.
But if you are new to the directive - I understand your frustration. It takes a while to get used to.
Oh, I see now. :)
Yeah, I'm quite new to this. And it's frustrating as hell.
First check if your application is excluded from the scope of PED.
Second you classify. You could use the PED category selector app or the PED calculator software form here:
Then, if your equipment is classified as not PED (<0,5 barg), art. 3.3 or cat I, you should follow another directive mentioned in art. I if applicable. If there is no other directive mentioned in art.I applicable, you have to apply the PED.
Thank you for your insight. I did not stumble upon this app, but as far as I can see, I don't fall under the PED directive. I do have a pressurized equipment (it IS a boiler with operating pressure of 2 bars, content: water), so I should fall under the Table 4 (this diagram in Annex II), but PS*V (4bar*110L) and the fact that is not a manual stoking device, excludes me from given directive.
Again, thank you all so much with the given informations. Kindest regards.
If it is a boiler it would be table 5 I think. And category III (2x110=220). But if it is excluded, you do not have to classify anyway.
I have no idea what a manual stoking device is however.
Table 5 is for steam boilers (superheated or "regular" steam), this is a warm water boiler, below 110°C. Manual stoking device means that the operator adds fuel for burning process by hand.