Per Unit Impedance 3 Winding Transformer for simple fault current calculation
Wfg42438
I wanted to see if anyone has a good reference of how to determine the per unit impedance of 3 Winding XMFRs ?
I have a very basic fictious system shown below and I'm trying to determine how to by hand calculate the LG and 3 Ph fault currents at Bus 23, 26, and Bus27 but I'm not clear on how to represent the 3 winding XFMR.
In the software package whats entered is :
MVA per winding
Zps, Zpt and Zst plus the X/R ratios.
Lets assume each lump load represents a 100% motor load
I found the following equations but cant seem to match the software's result which tells me im making a mistake when finding the three impedances they propose as :
Where im stuck is how to determine which of the three equations above to use to determine the equivalent impedances for the positive and negative sequence networks.
Something tells me that depending on the fault location some combination of these impedances applies.
Any guidance on this would be much appreciated.
Something to be aware of;
The delta will transfer power from the healthy phases to the shorted phase.
The current of this transferred power will be limited by the impedance of the primary to the delta and by the impedance of the delta to the secondary.
In the example, the total fault current is limited by the grounding resistor.
This is only important to show you that you are showing a three winding wye transformer and trying to use a formula for a wye/delta/wye transformer.
In your example, without motor loads, bus 26 and bus 27 could be treated independently and the third winding ignored.
The contribution of the motor loads complicates things.
With a single line to ground fault, the motors will continue to be powered by the two healthy phases.
The rotor will be developing equal back EMF on each phase.
This will back feed into the fault.
Additionally, the motors on the unfaulted bus will backfeed through the transformer to a fault on the other 13.8 kV bus.
Your challenge is to find the correct formula to determine the impedance between the 13.8 kV windings, and to determine the motor contributions.
How many times have we heard;
"Motor contribution to a fault will last for several cycles."
That is for a three phase short where the motor losses power and de-cellerates.
For a line to ground fault, the motor contribution may persist until the motor circuits are cleared.
And.- The motor contribution will be supported by the healthy phases.
Thank you for the insight is there any way you can point me to a good source to obtain the relevant impedance values for my particular case?
The positive and negative sequence impedances in a transformer should be equal. What is on the nameplate and/or test report?
Hi @Wfg42438,
The impedances Zps, Zst, and Zpt are obtained though a short-circuit test as you explained:
- Zps: Voltage applied on primary, secondary is shorted, tertiary is open. Therefore, Zps is the impedance between primary and secondary.
- Zst: Voltage applied on secondary, tertiary is shorted, primary is open. Therefore, Zst is the impedance between secondary and tertiary.
- Zpt: Voltage applied on primary, tertiary is shorted, secondary is open. Therefore, Zpt is the impedance between primary and tertiary.
These impedances represent the 3-wing transformer in a delta configuration. For short-circuit analysis, it is more adequate to use a wye configuration. To transform from delta to wye, you use the equations you showed.
Now, you need the basic information from the transformer so you can calculate the impedance values accordingly. Attention to ensure the per-unit base values are consistent during the calculation.
For the LG fault you will need to represent the SLD by its symmetrical components. The positive and negative sequences are the same for transformers, however the sequence zero changes depending on the winding type (wye x delta, and if the core construction is core-type or shell-type).
For a fault on each bus, you will easily find a different impedance driving different fault current values.
You can look for these references:
Symmetrical components and fault analysis: Book - Electrical Power Transmission System Engineering, Turan Gonen
This tutorial from SEL is also very useful: https://selinc.com/api/download/100688/
Well noted by @waross regarding the motor contribution during the fault.
Hope this gives a pathway through.