kaspor
Electrical
- Aug 12, 2021
- 45
Hello
I have the following data for a transformer in per unit which I need to convert to % impedance to enter into ETAP:
MVAbase = 55
Voltage base = 33kV
Positive & negative impedance LV-HV = 0.0030 + j0.1 per unit
Zero sequence impedance LV-HV = 0.002 + j0.06 per unit
To get this into % impedance:
Zpos(%) = sqrt(0.0030^2 + 0.1^2) * 100% = 10%?
Zneg(%) = sqrt(0.002^2 + 0.06^2) * 100% = 6%?
Are these the numbers I enter into ETAP?