Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

petroleum storage tank cooling ring water demand

Status
Not open for further replies.

nicolai

Mechanical
Joined
Sep 27, 2000
Messages
42
Location
NA
Hi there
We must calculate water demand for the cooling rings of 3 x 1,000,000 liter diesel tanks
I need clarity on few aspects:
Shall application rate be applied to the complete surface of all the tanks or only the portion which would be exposed to radiation heat? could the cooling ring discharge to only certain segments of the tanks?

is 10.2 l/min.m² as per NFPA 15 the industry norm?
The water demand amount to a huge figure.
any advice or opinion would be appreciated.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top