Hi Everyone,
I wanted to know the phase angle error limits for a C800 as per IEEE standard.
BCT type CT, primary 345kV, secondary 34.5kV for transformer
some test sheet values from SAT as below. Trying to ascertain if the value is acceptable.
1. CT is 600:5, 34.5kv side, phase angle error is +3.22 degrees.
2. CT is 1200:5, 345kv side, phase angle error is +8.76 degrees.
3. CT is 1200:5, 345kv side, phase angle error is +11.16 degrees.
4. CT is 600:5, 34.5kv side, phase angle error is +7.18 degrees.
The phase angle test values for the remaining CTs are less than 1 degrees