Phase Failure Test

Status
Not open for further replies.

Bronco425

Electrical
Apr 9, 2010
8
0
0
US
Hello,

I'm looking for a way to catch phase failures from the connections welding shut. My initial thought was to test all three phases for current after the connections were opened. If I still had current flow in any phase, then I would know if there was a weld. I was told that this would only work if at least two of the phases stayed shut. I was wondering if this is in fact true.

Thank you
 
Replies continue below

Recommended for you

Yes. True - sometimes, if you only have load between lines. But, if you have load from line to neutral, you will surely see current also if only that single pole is welded.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 