phase monitor

Status
Not open for further replies.

angryman

Electrical
Jun 20, 2006
49
in a typical 230vac 3-phase circuit with a motor contactor and overload and disconnect, where is a 3-phase monitor generally placed in relation to these items? I would guess before the disconnect, but I've guessed before on things.
 
Replies continue below

Recommended for you

I usually place it after the disconnect and before he contactor.
 
There are some nice power monitors used by the refrigeration industry. Some models include three phase voltmeters, recording of the last 25 faults, phase reversal, phase loss, voltage unbalance, timing functions appropriate for a hermetic compressor, and additional connections on the load side of the contactor to detect open or high resistance load contacts.
respectfully
 
cool thanks.....I leftit in before the contactor on the input basically because it fit nicely in my drawing there :)

Thanks for the comments!

Mark
 
There is an argument to be made for putting it ahead of the disconnect switch (with it's own separate disconnect and fuse protection). If the starter disconnect / breaker is interlocked with the enclosure door, the monitor may record every door opening as a phase loss (depending on it's internal power supply configuration). If you have one that does not have a fault buffer, you may lose the trip indication when you open the door to read it.

JRaef.com