LowSpark
Electrical
- Jan 31, 2015
- 23
I will begin with some facts and then ask the question.
Phase to Phase Voltages Lead Phase to Neutral voltages by 30 degrees.
Three Phase Apparent Power Equations:
If using Phase to Phase voltages:
S=1.732*V*I'
If using Phase to Neutral Voltages:
S=3*V*I'
Now when solving for the power and you know lets say the Phase to neutral voltage and its angle, why don't you multiply by 1.732 and add 30 degrees to it and stick that value into the Phase to Phase 3 phase apparent power formula?
For example:
V_L-n=120 @ an angle of 31 degrees
I*= 22 @ an angle of 20 degrees
V_L-L= (120*1.732) @ an angle of 61 degrees
Apparent Power Calc:
Using Phase to Neutral:
S=3*(120@31)*(22@20)= 7920@51degrees
Using Phase to Phase:
S=1.732*(208@61)*(22@20)= 7920@81degrees
As you can see the two apparent power calculations do not agree. The 7920@51degrees is in fact the correct answer. My question is, if Phase to Phase voltages lead Phase to neutral voltages, why don't you use this fact when solving three phase power with the Phase to Phase three phase formula? I mean you are supposed to put in the Phase to Phase voltage magnitude, why not the angle as well?
Phase to Phase Voltages Lead Phase to Neutral voltages by 30 degrees.
Three Phase Apparent Power Equations:
If using Phase to Phase voltages:
S=1.732*V*I'
If using Phase to Neutral Voltages:
S=3*V*I'
Now when solving for the power and you know lets say the Phase to neutral voltage and its angle, why don't you multiply by 1.732 and add 30 degrees to it and stick that value into the Phase to Phase 3 phase apparent power formula?
For example:
V_L-n=120 @ an angle of 31 degrees
I*= 22 @ an angle of 20 degrees
V_L-L= (120*1.732) @ an angle of 61 degrees
Apparent Power Calc:
Using Phase to Neutral:
S=3*(120@31)*(22@20)= 7920@51degrees
Using Phase to Phase:
S=1.732*(208@61)*(22@20)= 7920@81degrees
As you can see the two apparent power calculations do not agree. The 7920@51degrees is in fact the correct answer. My question is, if Phase to Phase voltages lead Phase to neutral voltages, why don't you use this fact when solving three phase power with the Phase to Phase three phase formula? I mean you are supposed to put in the Phase to Phase voltage magnitude, why not the angle as well?