MaxDmand
Electrical
- Dec 8, 2004
- 3
Can somenone verify this please - A 20kV/11kV 15MVA, YNd11 trasnformer is connected between a 20kV network and an 11kV switchboard. On checking the phase rotation at the 11kV switchboard it was found to be counter-clockwise. This was also the case on the 20kV side, which I suspected, due to some earlier situation on the same system. I suggested changing the phasing at the 11kV switchboard, but the contractor said he would rather do it on the 20kV line for practical convenience. After the change over (R/Y phases)the phase rotation on the 20kV side had changed to clockwise but the 11kV side remained counter-clockwise. Without making any more changes on the 20kV side, we changed the phasing on the 11kV side,; the result being that the phase rotation became clockwise. I am a bit non-plussed as I would have thought that the change on the upstream side of the transformer would have resulted in a similar change on the other side. I have done some vector analysis, drawn it out in autocad, but still don't seem to get an explanation. Any input would be much appreciated.