Phase shift for current limitting reactor

Status
Not open for further replies.

Schwatzernov

Electrical
Sep 5, 2006
47
Dear All,

Do anyone have experience with using current limitting reactor for limiting short circuit current in the system.
Someone said that using this reactor will cause 90 degree phase shift and synchronizing can not be possible without using some device to compensate this phase shift back to zero degree.
Is this understanding correct ?
Anyone, please advise.

Thank you

Schwatzernov
 
Replies continue below

Recommended for you

Since current through the reactor is zero before syncronizing, there is no phase shift. So no need to use any "device" to "re-phase" the system.


Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
You have to consider the impedance and the X/R ratio of the entire circuit. At normal current levels the impedance of the load will predominate and determine the power factor. (phase shift of the current.) It is only when a fault shunts all or part of the load and the currents are extremely high that the reactor predominates in determining the phase shift. If you were to "compensate" for the phase shift (possibly with capacitors) you would defeat the purpose of the current limiting reactor, at considerable expense.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 