jph90
Mechanical
- Jul 27, 2016
- 23
Hi guys,
Need some assistance on process design around a PHE I am looking to install. The HX serves to cool hot refined edible oil from 102 deg C to a nominal 45 deg C. The temperature of the outlet stream is not overly critical for any downstream processes, it is simply better for the quality of oil to store it at < 50 deg C following refining.
To achieve the cooling, the service fluid will be cooling water from the clients cooling tower. This circulates in supply/return headers at approx 60m3/hr, and i would be tapping off this to supply the required 12m3/hr to the HX for cooling. My question is - given that the temperature is not exactly critical (and it is acceptable for it to drop << 45 deg C as these are soft oils - will not go hard at low temps and viscosity is not an issue at low temps), is there a need for me to put a flow regulating control valve on the water supply line linked to a temperature transmitter on the oil outlet line? Wondering if this financial cost is necessary. What factors am i not considering? Is there a risk with feeding 60m3 unregulated to a PHE designed for ~12m3/hr?
Need some assistance on process design around a PHE I am looking to install. The HX serves to cool hot refined edible oil from 102 deg C to a nominal 45 deg C. The temperature of the outlet stream is not overly critical for any downstream processes, it is simply better for the quality of oil to store it at < 50 deg C following refining.
To achieve the cooling, the service fluid will be cooling water from the clients cooling tower. This circulates in supply/return headers at approx 60m3/hr, and i would be tapping off this to supply the required 12m3/hr to the HX for cooling. My question is - given that the temperature is not exactly critical (and it is acceptable for it to drop << 45 deg C as these are soft oils - will not go hard at low temps and viscosity is not an issue at low temps), is there a need for me to put a flow regulating control valve on the water supply line linked to a temperature transmitter on the oil outlet line? Wondering if this financial cost is necessary. What factors am i not considering? Is there a risk with feeding 60m3 unregulated to a PHE designed for ~12m3/hr?