Has anyone had practical experience with running long lengths of cable between a photoresistor flame scanner and a burner controller? More specifically a Siemens LAL2.65 and a QRB1 scanner. The documents say it can be run up to 200mtrs with RG62 coax. I have had some other advice not to use it over 20-30mtrs or there will be problems???
RG62 is a low capacitance coax (47.57pF/mtr) and an impedence of 93ohm. Also any of that coax is not robust and has a solid wire as its core.
As impedence and capacitance effect is to do with AC or a changing waveform which is more applicable with say self checking UV signals, I cant see why it would be critical with a simple photoresistor which is just a variable resistance passing a DC current of say 10-35micro amps.
I would like to use Dekoron screened cable which is more robust. Just for comparison a twisted pair version has a capacitance to ground of 141pF/mtr. Again saying is this going to be an issue with DC current? Resistance is not a problem as it is 13.7ohm/km.
Thanks in advance,
Rod
Rod Nissen.
Combustion & Engineering Diagnostics
RG62 is a low capacitance coax (47.57pF/mtr) and an impedence of 93ohm. Also any of that coax is not robust and has a solid wire as its core.
As impedence and capacitance effect is to do with AC or a changing waveform which is more applicable with say self checking UV signals, I cant see why it would be critical with a simple photoresistor which is just a variable resistance passing a DC current of say 10-35micro amps.
I would like to use Dekoron screened cable which is more robust. Just for comparison a twisted pair version has a capacitance to ground of 141pF/mtr. Again saying is this going to be an issue with DC current? Resistance is not a problem as it is 13.7ohm/km.
Thanks in advance,
Rod
Rod Nissen.
Combustion & Engineering Diagnostics