Pilaster: Column vs. Beam?
Archie264
993
I'm interested in the case where a pilaster is stiffening a free-standing exterior masonry wall, i.e., a "garden wall". The vertical load is only the pilaster's self weight. As I read the commentary in ACI 530-08, Sect. 2.1.7, it states that "Pilasters...can serve one of several purposes..." I infer from that that it may be treated as either a beam or a column (or a beam-column) depending on the application.
So...
1. May it be treated as simply a cantilever beam carrying the wind load when there's no significant vertical forces? It makes a difference in the minimum steel required.
...and...
2. Regardless of (1), how would you esteemed colleagues handle it?
Thanks.
X2 for beam.
Chalk another one up for beam.
It would be a beam column if it supported anything besides it's own self weight vertically.
Is it that large of a difference in steel? Don't forget that you can reduce your minimum steel for a column to 0.5% if you are stressed to less than 1/2 of the factored capacity.
That tightens the gap on the minimum steel argument.
I would likely put that much reinforcing in it. So I guess my answer could be, I'd analyze it as a beam, but I'd provide minimum column reinforcement. That way when they go to add something crazy to it I know there's capacity there. 4-15m verticals give you a 16x16 pilaster, seems reasonable to me.
Thanks, all. It seemed like a beam to me too but I was going through an approval agency's criteria and they required that all pilasters had at least the minimum column steel, so stated. Maybe they're a step ahead of things, a la Jayrod's recommendation? Or maybe that's their version of a safety factor? Who knows? In any case, thanks.
Take a look at the NCMA Tek 17-4B. It offers design information and some tables for masonry pilasters.