I need to get more insight into a typical pile driving criteria in this scenario:

A performed analysis concluded a pile tip elevation requirment for an H-pile which will be driven into many clay layers range from meduim to stiff clay layer (layers' avg SPT is 8, 20, and 35)

The questions:
1- Is a vibratory hammer can be used for the H-pile driving?
2- If yes, what is the type of the vibratory hammer that can be used or specified? (rpm, power/force,..etc)
3- How the pile driving criteria is specified "refusal criteria, etc.)"
4- In case the vibratory hammer will not be applicable(?), what are the typical hammer energy, blows per inch for refusal, are specified for impact hammers
5- How can I ensure that the driving stresses on the pile will not be exceeded with any of the above two types of driving.

Thanks

 
Replies continue below

Recommended for you

This thread has been sitting there, so I thought I'd state the obvious. If you don't have a Geotechnical Engineer on the project, experienced in pile design, you need to get one. There's a lot of guidance required in driving piles and you don't want to make a mistake on it. If the pile installers come out with the wrong equipment due to your specification, they're going to want a large change order to make it right.
I am in the final construction phases of a small (512 pile) project, and I don't know what I would of done without our Geotechnical Engineer (I'm structural). The GC tried to change our design based on the design being incorrect (it wasn't) and I couldn't of defended it as well as the Geotech.
 
adfo,
I agree with Jed - please get a local geotech to help you out. Pile foundations are too costly to mess with. If you only need this info for personal knowledge fine, but I would not advise you to design and establish driving conditions on your own. I have never used vibratory hammer to drive piles, except sheet piles - used automatic hammer, and desiel hammer.

There is a lot that goes into establishing the driving criteria, and this is normally verified by field testing using a PDA(pile driving analyzer). The PDA also monitors the stress in the piles.

* clay with SPT over 30bpf - i would classify as hard - not stiff.
 
for open profile H-piles - engineering news formula & diesel hummer. pile capacity must be confirmed by field load test on number of piles according your local code w/ necessary factor of safety to determine allowable load. an after all - just ask your geotech to do his part of job.
 
You can use a vibro to drive sheet piles, tubular piles or H piles. The effectiveness depends on the soil conditions.

Questions 2-5 depend on the pile design and the soil conditions. General replies wouldn't be helpful.

 
I agree with the sentiment that you need a geotech experienced in pile design for a project like this.

Having said that, I'd like to address a few of the issues you raised.

On sizing vibratory hammers, I spend a lot of time on the subject at


I also have a lot of other information on vibratory hammers at


If you're looking for a specific bearing capacity, a vibro isn't the answer. There's still no accepted correlation between the performance of a vibratory hammer and the ultimate axial capacity of a pile (as opposed to an impact hammer.)

With impact hammer, you're probably looking at a wave equation analysis, and that's where the experienced geotech is a must. PDA during driving will also call for someone who knows what they're doing.

 