Hutten
Civil/Environmental
- Jan 30, 2008
- 9
I am looking at structural design calcs for solar panel arrays to be constructed at our facility. The panel assemblies will be mounted on JIS piles vibrated into fresh pour 16" diameter reinforced high strength concrete piers.
Because of huge boulders on-site, the pile locations were first excavated and filled with a low strength concrete slurry (CLSM), then the CLSM was auger bored for the piers and piles.
The CLSM was batched with on-site soil, cement and water with a 200-400 psi design spec.
1. The structural engineer used LPILE and on-site soil properties from the original geo-tech report to design the pier depths and diameters, Lateral Bearing pressure = 325 pcf and allowable skin friction 285 psf/f. Shouldn't the design values be from testing on the CLSM itself, rather than the soil it replaced?
2. Some of the 28-day strengths of the CLSM were only 100-150 psi. The contractor will try to back into this value as adequate for the design. What should I look out for as to how this might affect the design and the pier / pile performance.
3. The structural provided computer print outs of the pier size design for horizontal and vertical loads. Should I also want to see uplift analysis?
4. Other questions will surely follow if you get trapped into this thread....
Thanks,
Denice, P.E. water industry California
Because of huge boulders on-site, the pile locations were first excavated and filled with a low strength concrete slurry (CLSM), then the CLSM was auger bored for the piers and piles.
The CLSM was batched with on-site soil, cement and water with a 200-400 psi design spec.
1. The structural engineer used LPILE and on-site soil properties from the original geo-tech report to design the pier depths and diameters, Lateral Bearing pressure = 325 pcf and allowable skin friction 285 psf/f. Shouldn't the design values be from testing on the CLSM itself, rather than the soil it replaced?
2. Some of the 28-day strengths of the CLSM were only 100-150 psi. The contractor will try to back into this value as adequate for the design. What should I look out for as to how this might affect the design and the pier / pile performance.
3. The structural provided computer print outs of the pier size design for horizontal and vertical loads. Should I also want to see uplift analysis?
4. Other questions will surely follow if you get trapped into this thread....
Thanks,
Denice, P.E. water industry California