Jacst3
Structural
- May 3, 2010
- 22
I am designing multiple steel framed structures to support equipment and piping. I am analyzing the structures in STAAD. There is debate on how to model the steel column bases: Fixed or Pinned. A truly pinned base usually results in excessive and unrealistic deflections. I have found a good compromise is to use fixed bases in the model, with partial moment releases at the bases for Mx, My and Mz.
A 1.0 factor equals no moment restraint. I've been typically using a factor of 0.9 or 0.95, meaning that the base is almost a pin. This seems to give reasonable results. The frames still require some bracing or moment connections to control deflections. Any comments or suggestions out there?
Thanks,
Jacst3
A 1.0 factor equals no moment restraint. I've been typically using a factor of 0.9 or 0.95, meaning that the base is almost a pin. This seems to give reasonable results. The frames still require some bracing or moment connections to control deflections. Any comments or suggestions out there?
Thanks,
Jacst3