zdas04,
I am unsure why you jumped on lfg2007 and yet have been strangely quiet while we have had numerous incorrect postings on this subject.
The posters on this forum come from all over the world so the ASME and API codes are widely used but as far as I am aware not the AWWA standards.
Comments by all are voluntary. Nobody gets paid to do this, hence some, if not many, posts go uncommented by the "regulars". Some days there are simply more important things to do. Some days you just don't feel like working for free, going to lunch, or going to bed. And some days, you just get tired of saying the same thing over and over. Sometimes you get to them before we do. Sometimes, its just pointless. Obviously the OP knows more about the problem than us talking heads do, so if he's building a water line to B31.3 and somebody tells him he isn't, the OP is free to ignore that comment and procede with building and testing to B31.3. I don't see a necessity to correct those kinds of comments (all the time). If some poster wants to waste everyones time by second guessing all the covenents and answering every permutation and exclusion to every permutation of every unasked question ... please leave me out of it. And sometimes the post has just moved off the first page. If that happens, I've usually lost interest by then and won't ever return to make corrections. Making corrections is tedious the first time, never mind in perpetuum.
Fortunately this morning I have a few minutes. You quoted out of context of the original post, so I will have to respond accordingly.
zdas04
"...'but pressure is pressure. If you pressurize a pipe to 150 psig with air or water, the induced stresses will be the same."
Incorrect - the stored energy of 150 psig of air is much more dangerous than 150 psig of water, that is why the same piping is tested to 1.5 x design pressure for hydrotest and 1.1 x design pressure (B31.3)and 1.2 x design pressure (B31.1) for pneumatic testing.
Energy density may be higher, but as zdas says, stresses are equal.
lfg2007,
Your 4 x less psi may have been misintepreted by yourself, pneumatic can be 40% less than hydrotest.
I'm not sure... and I don't feel like doint the math and responding. Sorry
Biginch,
"It is an excessive hazard that can only be used when hydros is not possible."
Incorrect - B31.3 states it can be done if a hydrostatic leak test is impracticable - not impossible.
I said "not possible", not "not impossible", The code uses "impractical" as you state, however, if you do attempt to avoid making air tests as I believe you MUST, and as you should in order to minimize risk of all kinds, impractical does in effect equal impossible, so I have no problem with the symantics that I used.
[/color]
"..must be 100% radiographed / Uted and structural welds examined via liquid penetrant, if an air test is done."
Please advise where in the code this requirement is stated ?
Please see Section 945.1, 2 & 3.
cvg
"If you mean to test a potable water system, you will not be using B31.3."
A talking head giving advice on some unjustified assumption that the OP can freely accept or ignore based on his more detailed knoweledge. Not a constructive comment in the first place, as its based on technically unjustified assumptions (even though the mathematical probability might be high) and, if I comment on that, it just makes me guilty of the same thing.
I am a Welding Inspector on the US$5 billion Goro Nickel Project in New Caledonia. I am a New Zealander working for a Canadian / Brazilian company in a French territory. We have miles and miles of potable and process water systems that are all fabricated and welded to B31.3.
You could just as easily have designed those water lines to no code, as cvg contends, and, as I have seen from South America to India, other or no codes for water lines are about a ZILLION times more common than B31., so simply on a probability basis cvg is correct
shmar
"If this is a fuel line you would not want to test it with water."
Fuel lines are hydrotested (with water) daily all over the world.
The only lines we do not hydrotest on site are sulphuric acid lines. (I am not a chemist but I think it is due to exothermic reaction)
[Being that you are in pipelines, I suspect you are quilty (as I often am) of thinking that the OP is talking about pipelines where water testing would be the norm, but the OP said "pipes". Perhaps Shmar thinks this pipe might be a fuel line on a A380 that needs to be tested in place. If so, who am I to argue? I know less about that than Shmar.
Why should zdas comment on that? I don't want to.[/color]
lfg2007,
Dependant on your code and whether the pipe is buried you may not even have to hydrotest.
If the test was 150 psig then you would presume the design pressure was 100 psig ( 1.5 x) which would make it Cat D in B31.3 and an ISLT only is required.
But you assume, without justification, that the OP is testing to B31.3
My suggestion is that EVERYBODY, READ the OP and concentrate on making a constructive comment to that rather than making outrageous assumptions, mentioning some obvious exclusion as a contradiction to another's post and arguing in perpetuum about the last poster's text. At least if nothing else of true engineering interest arose.
Deal?
PS No offence noted... or taken.
**********************
"Pumping accounts for 20% of the world’s energy used by electric motors and 25-50% of the total electrical energy usage in certain industrial facilities."-DOE statistic (Note: Make that
99% for pipeline companies)