Hello Gents,
I have an RFI from a contractor asking if he can use the same 150psi LSM electrical pipe trench flowable mix also below a large 36K transformer foundation over-excavation flowable fill. My concern is quality control of the mix and set time and well yes strength. The bearing pressure not a concern. However the over-excavation does extend 24" beyond the equipment and 24" below. Should I be concerned with shear strength for the 24" extending past the transformer footing. Am I over thinking this since even this low strength LSM mix is stronger that the subgrade in the first place? I feel compelled to increase the strength for at least to 500psi for no other calculated reason other than a higher chance of reaching a consistent compressive strength.
I have an RFI from a contractor asking if he can use the same 150psi LSM electrical pipe trench flowable mix also below a large 36K transformer foundation over-excavation flowable fill. My concern is quality control of the mix and set time and well yes strength. The bearing pressure not a concern. However the over-excavation does extend 24" beyond the equipment and 24" below. Should I be concerned with shear strength for the 24" extending past the transformer footing. Am I over thinking this since even this low strength LSM mix is stronger that the subgrade in the first place? I feel compelled to increase the strength for at least to 500psi for no other calculated reason other than a higher chance of reaching a consistent compressive strength.