valves4life
Industrial
- Feb 15, 2012
- 16
Hey everyone! I have been in a debate with one of our reps, regarding control valve sizing.
If I have a 12" line, and a 6" or 8" triple offset valve can do the required flow control (ie it has the CV and it isn't at too far opening angle), should I quote that? Is there a rule of thumb?
I was always told ISA best practices was not to drop more than 2 pipeline sizes below the line for a control valve. So in my example, the smallest valve should be a 12"er. However, I've tried to check this and the only thing I could find was in a book "control valve primer" by Hans Baumann, saying never go below HALF the pipeline size.
By the way, the media is water at ambient temp.
anyone have an idea what the right answer or rule is here?
If I have a 12" line, and a 6" or 8" triple offset valve can do the required flow control (ie it has the CV and it isn't at too far opening angle), should I quote that? Is there a rule of thumb?
I was always told ISA best practices was not to drop more than 2 pipeline sizes below the line for a control valve. So in my example, the smallest valve should be a 12"er. However, I've tried to check this and the only thing I could find was in a book "control valve primer" by Hans Baumann, saying never go below HALF the pipeline size.
By the way, the media is water at ambient temp.
anyone have an idea what the right answer or rule is here?